Re: Carrier A/C, Again!
How did you site subcooling only taking one reading?
Your numbers are backwards, you would have 30 degrees at 70, and 7 at 100...See the previous post..
This is true, except pumping pressures and superheat are on one side of a battle the TXV is trying desperately to win..
A txv won't open "to far" and stay there...They don't sit right at 12 degrees, they "hunt" you may have been looking when it was on the way back while it was hunting...If you have a good enough thermometer you can see the suction line go from 50 to 55 to 58 back to 55 to 50 and then back up, and do this over and over again...
Nope, there is no such thing as to far...The worst a system can do is run 0 superheat "totally flooding back" which is the most capacity you will get, but it will wipe out compressor valves...
I was in a hurry to head to work so I only got one reading. Might try both sides tomorrow depending on how my day works.
I think I understand the concept, dont worry too much about not having a board. Correct me if I am wrong.
How did you site subcooling only taking one reading?
1. A system using a piston (like my old evap) can only provide a steady flow of refrigerant to the evap coil. As the temperature rises the piston being static cannot increase the flow of refrigerant on by itself. This affect the efficiency of the system as the superheat of the system can be lets say 7 at 70 deg but 30 at 100 deg (just numbers there).
Your numbers are backwards, you would have 30 degrees at 70, and 7 at 100...See the previous post..
2. With a txv the flow of refrigerant into the evaporator coil can be changed. The valve drives its orifice larger or smaller depending on the temperature of the suction line (and other factors) attempting to keep the determined ideal superheat number.
This is true, except pumping pressures and superheat are on one side of a battle the TXV is trying desperately to win..
3. If the superheat number is high then you have what I been having, a system that is not delivering enough refrigerant to the evap to be balanced. If you get low numbers, like I did today, it probably means the valve has open beyond the ideal superheat and it is delivering to much refrigerant for the system to be balanced. When I say balanced i mean that point when you are delivering the maximum amount of liquid refrigerant to the evaporator coil and it gets evaporated by the evaporator load and (ideally, I think) there is no liquid refrigerant at the other end where it goes into the suction line.
A txv won't open "to far" and stay there...They don't sit right at 12 degrees, they "hunt" you may have been looking when it was on the way back while it was hunting...If you have a good enough thermometer you can see the suction line go from 50 to 55 to 58 back to 55 to 50 and then back up, and do this over and over again...
4. So that leads me to believe my valve just opened up too much today, probably influenced by the 115+ deg heat in the attic and maybe being not ideally insulated by me.
Nope, there is no such thing as to far...The worst a system can do is run 0 superheat "totally flooding back" which is the most capacity you will get, but it will wipe out compressor valves...