Hi I have a 40 amp breaker right at battery that goes to the 30 amp main breaker on 12volt panel is it necessary seems like overkill to me thanks
 

Attachments

  • 43D45772-CA95-4510-95A9-4504CFB0FEF7.jpeg
    43D45772-CA95-4510-95A9-4504CFB0FEF7.jpeg
    2 MB · Views: 7
  • 56C71530-1F20-4854-BD6D-AD4056BB609F.jpeg
    56C71530-1F20-4854-BD6D-AD4056BB609F.jpeg
    1.3 MB · Views: 6

dingbat

Supreme Mariner
Joined
Nov 20, 2001
Messages
15,528
Are the breakers in your home at the source (breaker box) or supply (wall socket)?

Breakers trip on downstream faults. Without the fuse on the battery that wire could ground and burn w/o tripping the breaker. The breaker protects the wire from the breaker to the panel

The head scratcher is the breaker. I can only assume they used it as an on-off switch. A simple in-line toggle switch is all that was needed to perform that action
 