Re: Blower vent line I/O
Here's a story from a few years back. And a good illustration of what can go wrong.
This was an aluminium Fisheries patrol boat that had just had some hull work done. The work was installing a new vent tube for the main under-floor fuel tank. Unfortunately the installer had no clue on how things should be, and installed the tube so it vented into the bilge
. Because the boat was having welding work done the fuel tanks had been emptied and before the first patrol needed to be filled. As the boat was at a remote location it was being filled from 200l drums (50 gallon barrels) and nobody was able to see a fuel spill from the vent line into the bilge. As SOP the bilge blower was switched on. This is when the whole lot went up, and because the explosion was in the bilge, the floor was forced up about 2 feet. The 2 guys on board were not killed, but they will never walk again. The floor came up with such force it destroyed their ankles and the bones in their lower legs.
The boat was shipped to the city for inspection and it was found that the blower wire had a VERY small chaff on it where it ran over one of the hull ribs. When the blower was switched on, the wire sparked and the fumes did the rest.
How do I know this?... I was the guy who did the inspection. It's a very sobering lesson when you see it first hand. Also as a Fisheries contractor I got to know a few of the operators. One of the guys hurt was one I knew. He had a young family, but will never be able to play or even walk with his kids.
Please, please... do the job right, listen to the advice here and do everything you can to minimize the risks. If that means spending an extra few dollars, do it...
When confronted by a choice of cheap or right I always ask myself "How much is my life worth?", then I think about the 2 guys on that Fisheries boat. Even if it's a few hundred dollars... I'd like to go out of this life, in many years time, with all my parts intact....
Chris........