Re: Blowers
I certainly don?t want Glen?s thread to turn into an argument, but there is a safety issue here and the discussion so far could potentially mislead readers of this thread long after it expires. I usually say my piece and shut up, even if someone else says I?m wrong, but the technical points made here warrant more serious consideration.
Smokeonthewater has replied that ducting the intake air to the area that accumulates fumes is a bad idea and that ducting is unnecessary, but if used, the ducting should be directed to the carburetor intake. I understand the point that directing air flow toward the vapours could disperse them to other points. I suggest that this will reduce the hazardous concentration of vapours to below an explosive level. But hey, I?m no expert, so I went on a quest to find the answer.
I haven?t been able to find a regulation or a discussion by regulators on the merits of not ducting the intake air to the low point of the hazardous vapour location. On the contrary, I?ve found only regulations requiring that two ventilation supply ducts are required to extend to the lowest part of the space. Smoke, perhaps there is a conflict between the two regulations that I found and another regulation that you are promoting. Please provide us with some legal support for ducting intake air to other than the low point of the hazardous space and maybe we?ll save someone some heartache. - Grandad
HTTP://CFR.REGSTODAY.COM/46CFR182.ASPX#46_CFR_182P460
AUTHORITY: 46 U.S.C. 3306; E.O. 12234, 45 FR 58801, 3 CFR, 1980 Comp., p. 277; Department of Homeland Security Delegation No. 0170.1.
SOURCE: CGD 85-080, 61 FR 986, Jan. 10, 1996, unless otherwise noted.
?182.460 Ventilation of spaces containing machinery powered by, or fuel tanks for, gasoline.
(a) A space containing machinery powered by, or fuel tanks for, gasoline must have a ventilation system that complies with this section and consists of:
(1) For an enclosed space:
(i) At least two natural ventilation supply ducts located at one end of the space and that extend to the lowest part of the space or to the bilge on each side of the space; and
(ii) A mechanical exhaust system consisting of at least two ventilation exhaust ducts located at the end of the space opposite from where the supply ducts are fitted, which extend to the lowest part of the bilge of the space on each side of the space, and which are led to one or more powered exhaust blowers;
From
http://www.tc.gc.ca/publications/en/...hr/tp1332e.pdf