Figure this one out and I'll buy you a beer!

Fed

Commander
Joined
Apr 1, 2010
Messages
2,457
Re: Figure this one out and I'll buy you a beer!

How does a loose connection pop a breaker unless the connection is on the breaker and the heat conducts into the breaker.
Short circuits and overloads pop breakers.
 

scutly

Petty Officer 1st Class
Joined
Aug 20, 2009
Messages
368
Re: Figure this one out and I'll buy you a beer!

loose connections can cause short circuits
 

pine island fred

Lieutenant Junior Grade
Joined
Dec 20, 2002
Messages
1,144
Re: Figure this one out and I'll buy you a beer!

I am with FED on this one. A loose connection will cause less current flow, not more. The problem was disturbed while he was isolating the different circuits. Also would not be the first time I saw a circuit breaker degrade and would not pass the rated current. Especially around salt water. regards FRED
 