High efficiency operation.
24 vollts is always present to the thermostat R terminal.
1.Thermostat sends 24 volts through white wire to furnace.
2.Furnace checks pressure switch, and safety switch's for proper positions (open/closed).
3.Draft inducer blower motor, starts to run.
4.If vent and vacuum hoses are clear the pressure switch, closes. (only a few pressure switch's open to prove venting)
5.After inducer blower purges the heat exchanger, either a pilot lights, a hot surface ignitor (HSI), or a spark begins.
6.If the furnace is an intermittant pilot model, once the pilot lights, current is sent through the flame by a flame sensor, if current is present through the flame the main gas valve opens and the burners ignite.
7.If the furnace is direct ignition, The HSI or spark ignites the flame. A flame sensor passes current through the flame, if current is present the main gas valve stays open and heat exchanger begins to warm up.
8.Most high efficiency furnaces then use an electronic timer on the circuit board to start the blower after the burners are proved.
9.Thermostat opens when desired temperature is reached.
10.The gas valve closes, burners extinguish, and the timer starts again to turn off the fan.