air con tripping main breaker

dave crooks

Recruit
Joined
Nov 4, 2012
Messages
3
Can anyone help with solving the problem of a 12,000BTU AIRRR conditioning unit which trips the mains power breaker when switched to heating cycle. It seems that the inrush current is high causing breaker to trip ???

Dave
 

Bondo

Moderator
Staff member
Joined
Apr 17, 2002
Messages
70,526
Re: air con tripping main breaker

Can anyone help with solving the problem of a 12,000BTU AIRRR conditioning unit which trips the mains power breaker when switched to heating cycle. It seems that the inrush current is high causing breaker to trip ???

Dave

Ayuh,... Welcome Aboard,... Is the breaker large enough to supply the demands of the heating element,..??

My guess is, it ain't...
 

JEBar

Chief Petty Officer
Joined
Aug 4, 2012
Messages
462
Re: air con tripping main breaker

as asked, what size breaker .... also, what other appliances are being operated at the same time ?

Jim
 

muc

"Retired" Association of Marine Technicians...
Joined
Jul 7, 2004
Messages
2,064
Re: air con tripping main breaker

Need more info on what system (reverse cycle or resistance heating) and control (three knob or digital) you have. You’re A/C owners manual will answer your questions – have you read it?

If it is an older unit with the 3 knob control, when switching from cool to heat you must shut it down for 5 minutes before switching to heat cycle to allow pressures to equalize.

If it is a newer model with digital control the equalize function is programmed into the control --- it’s possible somebody might have changed the program.

Or it’s possible the start capacitor on the compressor is getting weak. Or the circuit breaker is starting to go bad.

There are some more possibilities but the above are the most common.
 

dave crooks

Recruit
Joined
Nov 4, 2012
Messages
3
Re: air con tripping main breaker

as asked, what size breaker .... also, what other appliances are being operated at the same time ?

Jim

Hi Jim
the breaker is a B curve 16A 230volt , there is no other load at the time of starting. I am not certain of the total load of air con unit. The cooling water pump is 230v, 2pole 0.68kW Other than that I can not give much more info ??
 

dave crooks

Recruit
Joined
Nov 4, 2012
Messages
3
Re: air con tripping main breaker

Need more info on what system (reverse cycle or resistance heating) and control (three knob or digital) you have. You?re A/C owners manual will answer your questions ? have you read it?

If it is an older unit with the 3 knob control, when switching from cool to heat you must shut it down for 5 minutes before switching to heat cycle to allow pressures to equalize.

If it is a newer model with digital control the equalize function is programmed into the control --- it?s possible somebody might have changed the program.

Or it?s possible the start capacitor on the compressor is getting weak. Or the circuit breaker is starting to go bad.

There are some more possibilities but the above are the most common.

Hi muc
the unit was made around 1989, the gas has been checked and changed, there is no manual for the unit? but thanks for reply
 

Fl_Richard

Lieutenant
Joined
Jan 21, 2005
Messages
1,428
Re: air con tripping main breaker

Still need to know if it uses resistance heaters. With that said;

How old is the breaker? As they age they often start to break down and NOT handle their rated ampacity. An amp probe on the power leads during start up would tell the story and send you on the right path to solving the problem.


Exactly! Replace the breaker - then begin the quest for a deeper problem. Breakers get weak and trip prematurely.
 