LP lines on house Freezing

HVAC Cruiser

Lieutenant
Joined
Sep 12, 2009
Messages
1,254
Does anyone have any thoughts on the LP lines on my house freezing?

History:
I use very little LP, its just for the range top I have a convection over gas stove. This summer I got into an argument with the gas company that had been supplying my tanks.I use less than 100# a year, they wanted to charge me $700 a year whether or not I used the gas:mad:
I gave them back their tanks and installed 2 new 40# tanks and set the house up with a new regulator from the trailer and RV store, all has been fine till know. Last week my wife told me that we were out of gas so when I got home I swapped them over, still no gas. I used a hairdryer on the lines and regulator and viola we had gas again. I have now been going through this every day.

Here is what I'm thinking so far:
1- An LP setup is a pressurized,closed system there should be no way for moisture to get in.
2- The only way for moisture to keep re-appearing is the tanks were not purged properly on the initial fill there still being air in them causing moisture at dew point hence the daily freezing.

Anyone ever had this problem or thoughts on it?
 

Gary H NC

Fleet Admiral
Joined
Dec 1, 2005
Messages
8,972
Re: LP lines on house Freezing

I had that problem on my garage heater. When the temps get real cold the LP tank would freeze at the fittings...

Looking forward to the answers you get here..I never figured out why they freeze.I tried 3 different tanks.
 

rbh

Fleet Admiral
Joined
Mar 21, 2009
Messages
7,939
Re: LP lines on house Freezing

As was sayed if your propane isnt purged well enough you tend to get a air lock, I dont know why, but I flipped the tank up side down turned the valve, and depressed the ball lock mech, blasted out a second or two of propane, never had another problem, as for freezing up I dont think you have any problems till it hits -30/-40c (-40f is the same as -40c) at least thats about were it use to always plague us starting our trucks. As for the ice build up on the fittings thats the condinsation attaching and iceing it self to the fittings as the gas is already below zero.
rob
 
Last edited:

HVAC Cruiser

Lieutenant
Joined
Sep 12, 2009
Messages
1,254
Re: LP lines on house Freezing

As was sayed if your propane isnt purged well enough you tend to get a air lock, I dont know why, but I flipped the tank up side down turned the valve, and depressed the ball lock mech, blasted out a second or two of propane, never had another problem, as for freezing up I dont think you have any problems till it hits -30/-40c (-40f is the same as -40c) at least thats about were it use to always plague us starting our trucks. As for the ice build up on the fittings thats the condinsation attaching and iceing it self to the fittings as the gas is already below zero.
rob

Thanks RBH for your input, wow -40c I don't think its been that cold here since the ice age.
Flipping the tank over is a good idea, I'll try that. When you flip the tank over I imagine is the same as in refrigeration, your pushing liquid at that point which would push out any impurities.

I'm having the freezing problem from about 29f/-1.5c I figure it must be a freezing problem because the hair drier on the lines seem to do the trick. I initially figured doing it once would cure the problem by pushing whatever water was in it out but it is now an everyday problem
 

a70eliminator

Captain
Joined
Sep 9, 2007
Messages
3,688
Re: LP lines on house Freezing

A simple heat tape from the hardware store, or a modified crankcase heater mignt do the trick, never dealt with that problem before.
 

rbh

Fleet Admiral
Joined
Mar 21, 2009
Messages
7,939
Re: LP lines on house Freezing

I am thinking that if the tank was not purged correctly that could be a problem, as well if the lines got any condinsation in them between replacing the rental tank, they could freeze up, once you have the propane running freely, keep appliance on for a while and see if it starts to slow, just to be sure.
 

86 century

Ensign
Joined
Sep 8, 2009
Messages
986
Re: LP lines on house Freezing

It is a flow problem it is the same thing as cracking the valve will put a frost line on the tank from the pressure difference. You may be asking for more than the smaller tank has to give. I have the same problem with 20lb tanks on my salamander.
 

HVAC Cruiser

Lieutenant
Joined
Sep 12, 2009
Messages
1,254
Re: LP lines on house Freezing

RBH - I tried running the stove after heating up the lines, it works fine for a day. By the next morning its frozen again.

86 century -, I think your on to something there with it being a flow problem. I actually just go off the phone with one of my customers who's head of technical services for gas boiler manufacturer. He said the same thing basically, he said it is most likely a combination of the tank surface area at the top and the gas regulator valve. The gas regulator might be to small and that on a call for gas the velocity is to great causing it to push liquid instead of gas which is then freezing in the lines.

a70eliminator - I'm thinking you might have the simplest solution but is heat trace ok on a gas line
 
Last edited:

86 century

Ensign
Joined
Sep 8, 2009
Messages
986
Re: LP lines on house Freezing

Mine will do the same thing if it is 75deg in the garage(the tank is inside)so i dought the heat tape would work but.
 

Bucks45

Petty Officer 1st Class
Joined
Nov 13, 2009
Messages
342
Re: LP lines on house Freezing

As was sayed if your propane isnt purged well enough you tend to get a air lock, I dont know why, but I flipped the tank up side down turned the valve, and depressed the ball lock mech, blasted out a second or two of propane, never had another problem, as for freezing up I dont think you have any problems till it hits -30/-40c (-40f is the same as -40c) at least thats about were it use to always plague us starting our trucks. As for the ice build up on the fittings thats the condinsation attaching and iceing it self to the fittings as the gas is already below zero.
rob

I agree with RBH, airlock...anytime I've had that problem with the grill, I pull the line and drain some LP. It's always fixed it.
 

Howard Sterndrive

Rear Admiral
Joined
Nov 5, 2008
Messages
4,603
Re: LP lines on house Freezing

how was it concluded that the line is freezing?

sounds like you just aren't getting fuel through the line.
 

HVAC Cruiser

Lieutenant
Joined
Sep 12, 2009
Messages
1,254
Re: LP lines on house Freezing

how was it concluded that the line is freezing?

sounds like you just aren't getting fuel through the line.

it worked fine up till now all spring and summer etc, only started acting up in the colder weather. At first I thought the tank was just empty but when I checked it it still had 30# in it I have 2 40# tanks. On a hunch I hit the lines with a hair drier and in about 10 seconds of heat the gas started flowing again to the stove. I have had to heat the lines every day since Friday with the exception of today, I'm assuming that's because its 35 out today.
 

j_martin

Admiral
Joined
Sep 22, 2006
Messages
7,474
Re: LP lines on house Freezing

1. You don't want a heat tape anywhere near propane, unless yer into bomb making.

2. Propane will hit zero pressure at about -20 degrees F. The pressure you need is 11 inches water column, which is just a bit over 1/2 psi. If you disconnect the tank and crack the valve, you'll have plenty of pressure.

3. A cheap single stage regulator will sometimes act up when it gets cold. Moisture on and in the regulator can agravate the problem. Warming it up will help for a time.

4. Moisture in the tank, either from a supplier with wet gas, or from before the original fill can cause these kinds of problems. They pump liquid fuel from the bottom of the tank, and water is about twice as heavy as liquified propane.

I suspect a fresh regulator, and a simple structure to keep rain and snow from getting on the regulator will fix the problem.

hope it helps
John
 

Tim Frank

Vice Admiral
Joined
Jul 29, 2008
Messages
5,333
Re: LP lines on house Freezing

You have two things working against you.
The cylinders are supplying gas (not liquid), and the vapour pressure of propane at say 20 deg F is 1/4 what it is at 80 deg F. That is what "drives" your gas delivery at the stove and at this time of year can be as little as 1/4 of summertime "power".
The other constraint is obviously the length and size of supply piping.
Too long a run, and/or too small a diameter, and you have line-losses that coupled with the reduced operating pressure take the available flow below what will feed the stove.

It is possible that the lines are actually freezing, but that can only be from moisture...and most likely that would be an incomplete purge prior to filling the tanks initially.
To separate the two causes, next time you :"freeze up", get a tub larger than the in-service 40#er, and put the tank in it. Then fill the tub with warm water (75-90 deg F) to about 2/3 the cylinder height . If that solves the problem and gas flows, you have a system problem...as described at the top. You need bigger lines or bigger tanks....or both. Since presumably you are using the same lines as previously it would make sense that you need bigger tanks.

If the hot water does not have an impact, and if the hair dryer is used at the same constriction point each time and then results in continuous flow for a while, it may well be moisture in the system.

In either case the root change has been new tanks. IMO that is where to start....if the hot water does not work, take one of the tanks and have it "really" purged and then filled, and try that.
 

Tim Frank

Vice Admiral
Joined
Jul 29, 2008
Messages
5,333
Re: LP lines on house Freezing

1. You don't want a heat tape anywhere near propane, unless yer into bomb making.
:confused:
A check with any gas utility and/or competent gas fitter/contractor will prove that statement baseless.
As with any gas-related installation, it is critical to use the right equipment and the correct procedure, but this is a routine and safe design element in many service installations.

On the other hand, there should be no reason that heat-tracing these lines should be suddenly required, especially in the temperatures the OP reported.
 

dwco5051

Commander
Joined
Sep 14, 2008
Messages
2,326
Re: LP lines on house Freezing

The side of the regulator diaphragm that has the spring against it is vented to the atmosphere through a small orifice so if the diaphragm would leak it would vent to the outside at a controlled rate. It also pemits the regulator to work against the spring pressure alone. If the orifice is plugged by ice pressure can build up and cause it not to open. I had a service call to a school once where a fairly large natural gas regulator (2") was covered with ice from a leaking roof gutter causing it to close off and shut off the boiler. Don't know if that is your case but it just another idea. The vent on a regulator for a small propane tank is very small and could be frosting closed.
 

HVAC Cruiser

Lieutenant
Joined
Sep 12, 2009
Messages
1,254
Re: LP lines on house Freezing

Thank you all for your input,
Well its 27 deg here at 5:40am, I just checked the stove and there is no gas again. Guess its time for me to run some tests at 1st light. The run from the tanks is only about 15' and its 1/2" so I'm thinking that is ok for the rate of flow for the stove. That leaves either the tanks or the regulator being the culprit.
The regulator is a Marshall auto changeover 2 stage unit here is a link to the page were I got it from. What I am going to try is this, crack the line at the regulator from the tank, if I get gas there it is the regulator freezing, if I don't its the tank with moisture freezing up the feed lines. I'm starting to think going to be the regulator freezing up, I'll keep you guys posted to the finding
 

HVAC Cruiser

Lieutenant
Joined
Sep 12, 2009
Messages
1,254
Re: LP lines on house Freezing

Well it looks like the verdict is in, its a regulator problem. I cracked the line from the tanks at the regulator and there was plenty of gas and gas pressure. Looking at it I can see the tiny vent hole dwco5051 was talking about and water Can get into it the way I had mounted it, its horizontal right now. Looks like I am going to redo the setup to vertical making sure the vents face down then make a cover or pick one up to protect the entire setup from the elements. I think the trailer store might even sell the covers just don't know if they stock them
 

Bondo

Moderator
Staff member
Joined
Apr 17, 2002
Messages
70,464
Re: LP lines on house Freezing

Ayuh,... stepping in here alittle late,..
But,...
Contrary to what you'd think,...
Water in your propane is Not unheard of...
I've had the problem twice in the last 10 years, last year was the 2nd time...
Both times it took 2 things to relieve the Problem,...
1 was the gas co. injecting methanol into my tanks, then a warm spell to thaw the ice...
While my gas co. was adamant about the supposed fact that there's no moisture in their propane,...
But,... The methanol Cured the problem...
Maybe the next time you get your tanks filled, Ask 'em to inject a shot of methanol into each 1....

In my case, I have 2, 100lbers with quik-fills that are Mine, not theirs,...
Where they're mounted to the side of the house, there's water dripping onto the top of 1 of the tanks,...
Even though they're a sealed system, the quik-fill cap has a vent hole, which allows a tablespoon of Water to lay inside the quik-fill,...
When the delivery guy takes the plastic cap off,+ put's his fill adapter onto the quik-fill, that tablespoon of water is pushed into the tank...
I've since found 1 of the old aluminum tip-up covers,+ installed it over my tanks...

Btw,... The ice plug I was dealing with was in the 3/8" copper tubing, just before it entered the house, where it leveled out before dropping again...
 

Tim Frank

Vice Admiral
Joined
Jul 29, 2008
Messages
5,333
Re: LP lines on house Freezing

Did you replace the regulator after the tanks were changed?
If not, I wonder why this suddenly happened now, after all this time?
 